Jonathan,
Did you notice that your pool surface name is invalid?  It must the the name of the floor surface for the pool area (per the I/O Reference)
Inline image 1

On Sun, Nov 8, 2015 at 7:19 PM, Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Jonathan,
I have not reviewed your IDF in detail, but here are some ideas:
  • I'm guessing that because you've set the Pool Heating System Maximum Water Flow Rate = 0, that no pool heating occurs.
  • Inline image 2
  • I have not used the (relatively) new indoor Pool object in E+, but E+ needs to know at least a couple of things in order to calculate pool heating energy
    • a peak evaporation rate and 
    • a schedule for diversity of the evaporation (e.g., active vs. inactive periods in the pool)
  • Since evaporation represents a heat loss equivalent to ~950 BTU/hr, the load on the pool heater is the product of the peak rate and the diversity fraction.
  • If you have a dehumidification system, the evaporation is also a latent load for your dehumidification system.  This can be represented with an OtherEquipment object, as shown below (but may be included in some fashion by the Indoor Pool object).
  • Inline image 1
  • If you want to get more detailed, and assuming the pool is built into the ground, you might also consider defining the pool as a "basement" zone with walls of the same material as the pool sub-surface walls and a heating system which maintains that zone at the pool's water temperature
I hope this helps.

On Sun, Nov 8, 2015 at 6:18 AM, jduverge1979@xxxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Can anybody have a lot at what I'm doing wrong.

I am simulating an indoor swimming pool. I manage to get the project to simulate. However i cannot get the pool water temperature to 29 degree. And also there is no pool water heating rate. I thought maybe i have not properly identify the swimming pool (vertex). I compared mine to the swimming pool example provide 5Zoneswimming pool. In the example , the vertex use to reflect the surface of the swimming pool does not seems right as well.


I have attached the result spreadsheet and the idf file.

Can somebody please help


Regards

Jonathan




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

We will forever be crippled if we let emotion or unexamined reactions govern our thoughts and actions. 




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

We will forever be crippled if we let emotion or unexamined reactions govern our thoughts and actions. 



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___