|
Open cell for sure. In EnergyPlus you can probably leave everything on autosize and as default values, that are CTI rated conditions. - 95F entering water - 85F leaving water - either the default CTI OA wet bulb of 78F or (from approximate memory) 10F below the design wet bulb temperature, whichever is lower or something. It's further in appendix G I don't recall seeing anything in 2007 about two speed towers? Cheers Julien Envoyé de mon iPhone Le 15 mars 2016 à 16:14, "fpasserini.tn@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> a écrit :
__._,_.___ Posted by: Julien Marrec <julien.marrec@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |