90.1-2010, Appendix G3.1.3.11 states, “The heat rejection device shall be an axial fan cooling tower with two-speed fans, and shall meet the performance requirements of Table 6.8.1G.”

Table 6.8.1G gives the performance for open-circuit and closed-circuit towers but Appendix G doesn’t seem to specify whether one is to use an open or closed circuit tower in the baseline.  

 

 

cid:image003.png@01D09C46.E75BA0D0

Christopher Jones, P.Eng.
Senior Engineer

 

WSP Canada Inc.

2300 Yonge Street, Suite 2300

Toronto, ON M4P 1E4
T +1 416-644-4226

F +1 416-487-9766

C +1 416-697-0056

 

www.wspgroup.com

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Tuesday, March 15, 2016 10:58 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Re: Tables 6.8.1 - ASHRAE 90.1-2007

 

 

Open cell for sure.

 

In EnergyPlus you can probably leave everything on autosize and as default values, that are CTI rated conditions.

- 95F entering water

- 85F leaving water

- either the default CTI OA wet bulb of 78F or (from approximate memory) 10F below the design wet bulb temperature, whichever is lower or something. It's further in appendix G

 

I don't recall seeing anything in 2007 about two speed towers?

 

Cheers

Julien

 

 


Envoyé de mon iPhone


Le 15 mars 2016 à 16:14, "fpasserini.tn@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> a écrit :

 

Sorry, Jean. I am considering ASHRAE 90.1-2010 because I'm considering a LEED v.4 project. I wrote in the wrong discussion and I confused...

In ASHRAE 2010 for "Propeller or axial fan open-circuit cooling towers" the performance required is 3.23 L / (s*kW) while for "Propeller or axial fan closed-circuit cooling towers" the performance required is 1.18  L / (s*kW). For the baseline model according to Appendix G shall I consider the first value?



---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <jeannieboef@...> wrote :

Does 2007 differentiate? It's been a while...probably open loop. The closed loop tower possibly performs a little less effectively, but has other real world advantages. I'm betting the performance gap is small, but don't have any experience to say for sure.

On 14 Mar 2016 3:37 pm, "fpasserini.tn@... [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 

Other questions relative to Table 6.8.1G of ASHRAE 90.1-2007:

- for the baseline model (System 8) shall I consider "open-circuit cooling towers" or "closed-circuit cooling towers"?

- how could the required performance be imposed in EnergyPlus? I'm using the object CoolingTower:TwoSpeed

Best Regards

 



You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance@xxxxxxxxxxxx so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership


__._,_.___

Posted by: "Jones, Christopher" <Christopher.r.Jones@xxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___
Email file not found:
C:\Users\lklawrie\Downloads\Embedded\image00515.jpg
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\image0064.jpg
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\image00723.jpg