[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: Setpoint manger control for a BASELINE system-6 (packaged rooftop VAV with reheat)





For 90.1 modeling, as you said earlier baseline supply air flow rates shall be based on supply air to room air temp difference of 20 F i.e. 11.1 C. In Sizing:system, 'Central Heating Design Supply Air Temperature' is the design supply air temperature at heating coil outlet i.e. AHU outlet. So this has to be thermostat heating setpoint + 11.1 to meet 90.1 modeling requirement. Heating coils will be sized using this information and will have to be oversized by 15% to meet G3.1.2.2 requirements. This is my understanding.

p.s. One quick comment regarding max PIU secondary flow rate to be 50% of primary air flow rate. EMS may be able to provide some help but I couldn't explore it well. If I find some solution for that, will share it here.

On Fri, Apr 29, 2016 at 12:09 PM, telemar87@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Thanks Chandan for your adices,

there is just one thing I don't agree with. Why should I size the cental heating air flow with a 31°C (20°C heating zone SP +11.1°C)  temperature when, during the simulation I'll have a central heating temperatureof  max 17.78°C due to the setpoint manager?

In my opinion, using a 17.78°c as central heating temperature seems to be sufficient. In this way, the central AHU works just in a cool or preheat mode, while the 100% heating is reached by the PIU units.  




--
Chandan Sharma
Principal, Convergent Solutions


__._,_.___

Posted by: Chandan Sharma <chandangsharma@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___