Re: [EnergyPlus_Support] RE: EnergyPlus humidification control





ducted return would be negligable. at a duct speed of 4m/s...
Q=VA so for worst case DN100 pipe that's = 4 x 0.00785 = 0.0314 m3/s = 113 m3/h
if you had a 3 W LED spot every meter...
E=0.35*Q(in m3/h)*dT
so dT=0.075 Kelvin
and that would be like having the light sitting in the pipe!

with old lights (halogen spots) at 25 W per spot, the same check would yield 0.63 K.

Jean


On Mon, 4 Mar 2019, 16:15 'Edward G. Lyon' eglyon@xxxxxxx [EnergyPlus_Support], <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

If you had a return air plenum, some lighting and building load can be assigned to the plenum and reading that air RH would be shifted.  The room conditions at a return node are a â??well-mixedâ?? condition for the room that is as close as you can get to a room condition.  Displacement ventilation would be a wild card as I donâ??t know how latent loads get introduced.

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER
781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com

Send Files

From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, March 4, 2019 8:34 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Cc: Jim Dirks <jim@xxxxxxxxxx>
Subject: [EnergyPlus_Support] Re: EnergyPlus humidification control

 

 

Christopher,

The zone average %RH sounds like it would be pretty darn close to me. (closer by far than "not possible"). If the Baseline and Proposed models apply the same method, the comparison should be spot on, I think. 

 


From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx> on behalf of 'Jones, Christopher' christopher.r.jones@xxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, March 4, 2019 8:08 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Cc: Jim Dirks
Subject: [EnergyPlus_Support] RE: EnergyPlus humidification control

 

 

Thank you Jim,

Given that the return air stream may include pick-up from the lights, would not the return RH be slightly less than the average zone RH? It likely wouldnâ??t be significant.

 

Christopher R Jones, P.Eng.

T+ 1 416-644-0252

 

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Friday, February 15, 2019 4:57 PM
To: 'Jones, Christopher' christopher.r.jones@xxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Subject: [EnergyPlus_Support] Re: EnergyPlus humidification control

 

 

Christopher,

I'd suggest that the modeler use:

 - for a multiple zone system:  SetpointManager:MultiZone:MinimumHumidity:Average 

 - for a single zone system:  SetpointManager:SingleZone:Humidity:Minimum

 

"Officially", E+ is not measuring humidity at the return air node, but it's doing effectively the same  thing by determining the zone return air humidity.


From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx> on behalf of 'Jones, Christopher' christopher.r.jones@xxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Friday, February 15, 2019 2:16 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] EnergyPlus humidification control

 

 

I am reviewing a LEED 2009 submission. The design sequence of operations calls for humidification to be controlled by measuring the return air stream RH. The modeler states that it is not possible for EnergyPlus v9.0 to model this control strategy. Is this the case? I am used to IES where it is possible with a few clicks.

 

Christopher R Jones, P.Eng.

T+ 1 416-644-0252

 

 

 




NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited...... If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance@xxxxxxx so that we can promptly address your request.. Note that not all messages sent by WSP qualify as commercial electronic messages.

AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap@xxxxxxx afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.



-LAEmHhHzdJzBlTWfa4Hgs7pbKl



__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___