[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Pump on Demand Side = True ?





Edwin,

Thanks for your reply. Also, is there any news on the inclusion of a VRV module in the upcoming E+ release?

Vinay

On Fri, Apr 1, 2011 at 10:39 AM, Edwin Lee <leeed2001@xxxxxxxxx> wrote:
 

Vinay:


Right now that is true.  A future release will merge all plant and condenser features together, so that you will be able to use a primary/secondary system in condenser loops.

Edwin


On Thu, Mar 31, 2011 at 14:05, Vinay Devanathan <vinay.devanathan@xxxxxxxxx> wrote:
 

Edwin,


Is it only possible to place a secondary pump in a Plant loop using Common Pipe simulation? Is it not possible in the case of a condenser loop?

2009/12/4 Mário Neves <m_neves32@xxxxxxxxx>
 

Thank You One very mutch for the help.
 


From: Edwin Lee <leeed2001@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Fri, December 4, 2009 4:39:34 PM
Subject: Re: [EnergyPlus_Support] Pump on Demand Side = True ?

 

MN:


There can only be a demand side pump if there is a common pipe simulation in place, in which case there will be both demand and supply pumps.  The pump cannot be passive, because it will always want to be the component setting the flow.  

You may be able to approximate the energy consumption if you know the required flow rates throughout the simulation and can approximate the pump head.

Edwin Lee
EnergyPlus Development Team

On Fri, Dec 4, 2009 at 10:35, Mário <m_neves32@yahoo. com> wrote:
 

Good Afternoon Fellow Energyplus Users

Does anyone know if it´s possible to place a pump in the demand side of a plant network? The pump will be passive placed in series with an active component like a ZoneHVAC:BassBoard. I just want the energy consumpion of the Pump.

Thank You Once Again
MN








__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17230)
http://www.pctools.com
=======