[EnergyPlus_Support] Re: Easy question - Very thick massive external floor
Just a follow up post. I have made some (simplified) sums. Turns out the conductivity of this very thick slab is (obviously) dependant on the Temperature at my radiant floor internal source (32 deg C) and the outside external floor surface area (ceiling of underground parking open to outdoor air, somewhere between -12 and 18 deg C).
At the -12 deg C scenario, results in steady state conduction of about 9 W/m2.
At the more likely 18 deg C scenario, results in steady state conduction of about 3 W/m².
My conclusion is that heat transfer is not adiabatic enough to use this solution (applicable better when the dT is almost zero).
I'm running a simulation ATM (with the conversion errors) and reporting the inside temp after the main insulation layers to see if a pattern for the Temp here emmerges that i can use for the otherside coeff solution path.
Will report back when I find some time.
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/