I found out the issue is:
"The zone loads are sensible-only, and do not include ventilation loads. Also, the "calculated" loads (and those in the zsz file) do not include any sizing factor. The component sizing includes factors to actually size system coils and equipment-- such as sensible, latent, ventilation loads, and sizing factors."
Jeremiah D. Crossett | Senior Analyst | Phase Change Energy Solutions
120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
On Fri, Sep 14, 2012 at 1:54 PM, Jeremiah Crossett
<jcrossett@xxxxxxxxxxxxxxx> wrote:
YI, sorry to have had your name wrong- the tables with the highlighted values again are-Report: ComponentSizingSummary
ZoneHVAC:IdealLoadsAirSystem
|
| Maximum Heating Air Flow Rate [m3/s] | Maximum Cooling Air Flow Rate [m3/s] |
Maximum Total Cooling Capacity [W] |
| ZONE1AIR |
0.013146 | 0.058907 | 1007.43 |
Report: HVACSizingSummary
Zone Cooling
| Calculated Design Load [W] |
User Design Load [W] | Calculated Design Air Flow [m3/s] | User Design Air Flow [m3/s] |
Design Day Name | Date/Time Of Peak | Temperature at Peak [C] | Humidity Ratio at Peak [kgWater/kgAir] |
| BLOCK1:ZONE1 |
792.83 | 792.83 | 0.059 | 0.059 |
LOS ANGELES INTL ARPT ANN CLG 1% CONDNS DB=>MWB | 8/21 16:32:00 | 26.28 | 0.00955 |
Jeremiah D. Crossett | Senior Analyst | Phase Change Energy Solutions
120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
On Fri, Sep 14, 2012 at 1:49 PM, Jeremiah Crossett
<jcrossett@xxxxxxxxxxxxxxx> wrote:
Jason, Thanks for your input it was very helpful.
YI, thanks for your response- however Apparently did not read the post or look at the tables because the values you sent have nothing to do with the discrepancy between the
Maximum total cooling capacity" and the "calculated design load" The values in question are highlighted in yellow and make up a rather large discrepancy is not from a sizing multiplier.
The questionable values are
- Calculated Design Load [W]=
792.83
- Maximum Total Cooling Capacity [W]=
1007.43
- Delta [W] = 214