RE: [EnergyPlus_Support] Re: Calculated load different from component sizing summery





 
I usually respond to items I know.  I saw your whole page of EPlus reference to the HTML, therefore I pointed out that "user" meant "User spedified".  I did not know where the other number came from, and therefore did not respond.  My PC is too slow to run your IDF with weather file simulation.
 
Now I know that  it is the result of the IdealLoadsAirSystem I can simply say that this Maximum Total Cooling Capacity has no relationship with the DesignDay sizing value, because the former is from running the weather file data, and mayl be the same value, if you use the extreme day weather file data for sizing.. 
 
There is no pupose in comparing two numbers which are known to be from different conditions.  If you have used the 0.4% DesigndaySizing object, the difference value would be smaller.
 
As you have already found "your explanations", you need not comment or agree with what I said above..
 
  

 Dr. Y.L. Li  

 

To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: jcrossett@xxxxxxxxxxxxxxx
Date: Fri, 14 Sep 2012 13:54:22 -0700
Subject: Re: [EnergyPlus_Support] Re: Calculated load different from component sizing summery

 
YI, sorry to have had your name wrong- the tables with the highlighted values again are-
Report: ComponentSizingSummary 
ZoneHVAC:IdealLoadsAirSystem
Maximum Heating Air Flow Rate [m3/s]Maximum Cooling Air Flow Rate [m3/s] Maximum Total Cooling Capacity [W]
ZONE1AIR 0.0131460.0589071007.43
Report: HVACSizingSummary 
Zone Cooling 
Calculated Design Load [W] User Design Load [W]Calculated Design Air Flow [m3/s]User Design Air Flow [m3/s] Design Day NameDate/Time Of PeakTemperature at Peak [C]Humidity Ratio at Peak [kgWater/kgAir]
BLOCK1:ZONE1 792.83792.830.0590.059 LOS ANGELES INTL ARPT ANN CLG 1% CONDNS DB=>MWB8/21 16:32:0026.280.00955



Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions
120 E. Pritchard St.  | Asheboro, NC 27203  | Mobile 503-688-8951
 
  






On Fri, Sep 14, 2012 at 1:49 PM, Jeremiah Crossett <jcrossett@xxxxxxxxxxxxxxx> wrote:
Jason, Thanks for your input it was very helpful. 

YI, thanks for your response- however  Apparently did not read the post or look at the tables because the values you sent have nothing to do with the discrepancy between the
Maximum total cooling capacity" and the "calculated design load"  The values in question are highlighted in yellow and make up a rather large discrepancy is not from a sizing multiplier.

The questionable values are 
  • Calculated Design Load [W]= 792.83
  • Maximum Total Cooling Capacity [W]=  1007.43 
  • Delta [W] = 214











__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___