[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Annual Peak cooling variable ?





Li, Please refrain from responding to my posts, (and others beware) your responses are un-founded and incorrect. You waste time arguing and make presumptions without actually looking at users files or understanding the issues. 

Response to your lie.
 
Most of your IDF did not run, because they are  not complete.
 



Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions
120 E. Pritchard St.  | Asheboro, NC 27203  | Mobile 503-688-8951
 

  






On Fri, Sep 21, 2012 at 11:04 AM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
 


I have no comments on your new questions.  They are not really related on what I have commented on the topic.
 
 


I like the 5 zone model and doing DesignDay sizing as the system  and IDF verification tool.
 
Most of your IDF did not run, because they are  not complete.
 
 Dr. Li  

 
Date: Fri, 21 Sep 2012 10:27:52 -0700

Subject: Re: [EnergyPlus_Support] Annual Peak cooling variable ?

 
Here is a question-- I see no practical use for the sensible cooling rate in its current annual average approach- does anyone have any use for this annual average cooling rate> if not then the variable should be depreciated and replaced with a variable that shows the annual peak so that this variable can be used for load minimization. 

If you where to have a $ value tied to your hvac and output to csv than you could have the same but more direct effect as you could glean from an annual peak- However the annual peak is now in the eso file so it should be the easiest to add to the idd/rdd a variable titled "sensible cooling rate peak" Appending by hand would not work for large studies due to the imperfect nature of thousands of copy pastes..  (jE+ could append automatically with rvi if there was a variable that matched).. To write a script is one solution. But given the strait forward nature of the problem, the usefulness and simplicity of the solution it just makes most since to include this in some future version of e+.  

Thanks Li, 
I wonder sometimes by your comments if you are serious or if you do this for fun- Also from what I have seen of your posts you just use the 5 zone model with ddy runs only, not something I see as being much like a real building. My single zone studies are designed to be as detailed as the software is capable of for that single zone. 

By the way the reference buildings in the example folder is not climate specific such as the user requested.

Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions
120 E. Pritchard St.  | Asheboro, NC 27203  | Mobile 503-688-8951
 

  






On Fri, Sep 21, 2012 at 7:20 AM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
 


Sorry, Jeremiah
 
My comments are straight forward.  I do not 'insinuating about "one window of partial construction" '.   That is what I found in your IDF.  To me it does not look like a part of  an energy saving building.
 
As the maximum peak values are in the ESO , you can open the file one by one and append the values to the .csv.  If you are asking the EPlus parametric run to create your exmple.csv, that is another request.  It has nothing to do with the normal EPlus simulation run, nor the .rvi post processor.
 
Every post you make in the forum introduce something different.  That is your problem.  HVAC component cost, initial cost, etc. has nothing to do with PCM nor maximum peak values.
 
You are the PCM EPlus optimization expert, so do your own research and do not ask me any more.   I am not looking for a fee,in case some one is still watching.
 
What else do you want me to add to your comments?   By the way the reference buildings are in the ExampleFiles folder.
 
 Dr. Li  

 
Date: Thu, 20 Sep 2012 13:57:11 -0700

Subject: Re: [EnergyPlus_Support] Annual Peak cooling variable ?

 
Dr. Li 

Thanks- I actually do have the full model of this projects well, but what I do is study individual zones in great detail and am not sure what your insinuating about "one window of partial construction"  The CSV file shows 960 iterations of the model I sent and the annual output variables in a single sheet automatically created with the original problem of the sensible cooling rate being the average number rather then max. I would love to hear about your "several different ways to use PCM's" other than the between insulation and interior surfaces of external adjacency's if you could share?  (I have not found better results with any of the other options I have experimented with...:)


Best



Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions
120 E. Pritchard St.  | Asheboro, NC 27203  | Mobile 503-688-8951
 

  






On Thu, Sep 20, 2012 at 1:31 PM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
 


Sorry, Jeremiah
 
I do not want to discuss this topic any more.
 


 
I have no idea how you do the modelling, and have no interest in using the PCM material in a wall or roof as in your IDF..
 
Yes, I have several different ways of using the PCM storage material, and the way to use it correctly in a wall. 
 
Have your fun with parametric runs, on one wall and one window of a paartial buiding geometry..
 
Bt the way, the sample csv file you send me does not contain any useful information.  I am not going to tell you why, because there is  not inough information on the chart for me to comment on what the values represent.  So long they mean something to you, it will be fine.

 Dr. Li  

 
Date: Thu, 20 Sep 2012 13:10:53 -0700

Subject: Re: [EnergyPlus_Support] Annual Peak cooling variable ?

 
Dr. Li, 
Either you have not looked at this model, or need to learn how the surface adjacency of Energy Plus works- as the floor is "surface" so the boundary conditions are "surface" with the identified surface being the name of the same surface.  The South, North and East walls are internal- as is the floor. The external adjacent to exterior are roof/ceiling and west wall. The model shows a 16% cooling load reduction, and 35% cooling energy consumption I think that is rather good.  The dollar per kW numbers for cooling system size are just to fill blanks, and change for each building.  I have just one more question for you-  The most typical PCM applications are inside of insulation, as shown in the model I sent-- how do you imagine might be a better application of PCM such as attached image than between insulation and drywall as configured in this model?



 



Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions
120 E. Pritchard St.  | Asheboro, NC 27203  | Mobile 503-688-8951
 

  






On Thu, Sep 20, 2012 at 5:26 AM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
 

Hi, Jeremiah
 
I do not think that I need to continue with this topic with you.

 
"First I must mention that the adjacency of the surfaces with PCM are external-"
 

There is no wall or ceiling  in your building that is internal.  Floor is also to ground. The PCM layer is insulated from the exterior, as is in the inner layer next to the dry wall.  Is this the best way to add the PCM?

 


I know what is EPlus, and how .rvi etc are to be used.  I know what is in the SQL script.  All the data in the ESO are in there.

 

I do not run simulation like you do and am not interested in the common .csv, unless it has some meaningful results.




 
I have a generic value of $2000 per Ton for chiller provided to me by a user and research, for projects the number changes - what is useful is to be able to use a number, as I have no problem getting the bid price for actual systems or using generic figures for generic models.
 
 
I already mentioned that.  Call a tender to get all you want.  Why bother to add it to the simulation which is mainly for the building and not for the equipment.  Eplus is not designed for material research, either.  But it is a good tool to provide a controlled environment to test the material when used as a building material.  May be you do not know how to this.  I am not willing to discuss with you on this topic.
 
The generric cost  number does not mean anything.  It varies from place to place and does not hold for the different configuration of the same equipment type.  .  The number you quoted in you example for the DX coil is well to high.  $5,700 for a 1000w coil.  $5.7 for 1kW is too low.
 
 
If yu think they should be included, go ahead.  I do not care about the cost output in the EPlus, as they do not apply to my county.
 


Go ahead and do what you want and ask what you want.  You are the bioPCM expert, and I do not think I would use the biostix your way. 
 
In fact, I am not really interested in HVAC system  for general use.  Only special buildings with special  application requirement would need customed HVAC.  Comfort is not one of the requirements.
 
 
 Dr. Li  

 
Date: Wed, 19 Sep 2012 19:16:40 -0700

Subject: Re: [EnergyPlus_Support] Annual Peak cooling variable ?

 
Dr. Li, 
This is fun- you make me really work to make my point-thanks---  I guess I should have mentioned that I am useing jE+ as it provides the ability to populate values from E+ variables- (more on this below)
  • My bullet point comment on your other comments-
Ice has the heat  storage and release effect at 0°C. 
  • This exzample model uses BioPCM with a melting temp or Q value of 27c for the roof and 25c for the external wall.
 Because the values are already in the ..zSz.csv file, which is smaller and easier to extract.  So, why making the live more difficult. If you have the parametric file name set up in a list, a loop can open the  zSz.csv, go to the last line - 2 and pick out the values, and append them to a new file in the format of your choice. The peak values are automatically generated in the sizing file and no .RVI file is needed.  The normal .csv file would only accept a single value data for each column.  Therefore, the peak value cannot be sent there.  You can ask the developer to change the averaged value to peak, then will also show automaatically in a annual listing.  May be be both as two single field data.
.

6.1.3 RVI/MVI file ? in the EnergyPlus package, a utility (ReadVarsESO, see E+ InputOutputReference) for extracting variable and meter values from the E+ output files (?eplusout.eso? and ?eplusout.mtr?) is provided. It will produce a more usable data table in CSV format. To use this utility, you need to specify a RVI or MVI file, which defines the source and variables to be extracted with ReadVarsESO. See 6.1.3 for more particulars of this file. 7.6 Result and Report Tables EnergyPlus simulations can generate large amount of output. Rarely all of these information are required for (especially) a parametric study. A good practice is to define as few output as possible in the EnergyPlus models, and to extract exactly the information required for further analysis. jEPlus will collect CSV tables from each job directory, and compile a single table containing all results from the batch. The summary data table is named ?SimResults.csv? and is stored in the Work directory. Also stored are ?RunTimes.csv? and ?SimJobIndex.csv?, which contain EnergyPlus simulation error count and CPU time, and the corresponding index table of the jobs. Full Job Index files can be generated using the ?Create Job Indexes? command on ?Tools? menu. A number CSV files will be generated, along with a SQL script that creates all tables in the job index database.

You would need a common .csv file for the 100 plus run.  The .csv in one simulation will not show all the values.  The data you need are in two places, .ESO  and   ..zsz.csv automatically without making a output request. Even if you have the value in the main .csv file, you will still need to collect them from 1000 plus .csv files.
  • See attached example of a common csv file from a 100 plus run. jE+ does this automaticly as well as has provides Min/Max post processing. Again the problem is when Energy Plus outputs Sensible Cooling Rate as an annual average it does not 

Component cost is never an element in the EPlus simulation input.  Even in an manufacturing factory floor, it is not possible to get the component cost.  You can try contacting Carrier, Hitachi, or GE and find out whether they can provide you with the DX coil cost, even if it is a replacement  part for a current unit.
  • I have a generic value of $2000 per Ton for chiller provided to me by a user and research, for projects the number changes - what is useful is to be able to use a number, as I have no problem getting the bid price for actual systems or using generic figures for generic models.
  • The ability to model costs is currently in E+.. See Energy Plus documentation component cost line item InputOutputRefrence page 1775, and the idf I provided as an example-- the need would be to have this output as a variable rather then just to HTML, and if possible to be able to report a value per calculated heating or cooling load (possibly this was not included back when you read all the manuals) ComponentCost:LineItem Each instance of this object creates a cost line item and will contribute to the total for a cost estimate. Each line item is reported in table form in the tabular report file. The user must request that this report be generated by including a Output:Table:SummaryReports object with the Component Cost Economics Summary option selected. The style of a tabular report can be controlled using the OutputControl:Table:Style object. Cost estimates are not currently general in that they cannot be performed for every type of component that could be included in an EnergyPlus model. Although a ?General? option is available where all information needed for the cost line item is input by the user, the usefulness of cost modeling within EnergyPlus is expected to be enhanced when quantities are obtained from elsewhere in the input file or computed during a simulation. The cost computations are programmed in selected ways for selected objects. The objects available and the type of cost modeling that may be performed are discussed in detail in the discussion of Reference Object Type field. A particular instance of this object will always have many blank fields. Entering values in too many fields may cause an error because the program may determine how a particular cost is to be calculated based on the presence of non-zero values in particular fields. The input object includes fields that are reserved for future use in expanded cost estimate and investment analyses planned for future versions of EnergyPlus. If you would like to request additional objects or different methods of modeling component costs, feel free to describe your needs and submit a request via email to energyplussupport@gard.com.
All the cost in the EPlus are fuel and electricity cost calculated from the demand, and adjusted for efficiency performance, schedules (Season,Off peak, etc.), different locations, etc.  They are there mainly for LEED certification.  They have nothing to do energy conservation design.
  • These are something I have been meaning to use in tandom with component cost line item for ROI projections  thanks for the reminder. 



Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions
120 E. Pritchard St.  | Asheboro, NC 27203  | Mobile 503-688-8951
 

  


 




































__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___
Attachment not found:
d:\eudora\attach\gas-Exzample_For_Dr_Li_DDY.idf