Thanks Karen. I used 99.6% heating design conditions for WinterDesignDay and 1% cooling design conditions for SummerDesignDay from the weather file in the SizingPeriod and also changed it in the schedules and it works, but I'm just curious to know why it doesn't size using the typical conditions from the weather file.AberSent: Tuesday, January 22, 2013 5:55 PM
Subject: Re: [EnergyPlus_Support] Calculated cooling and heating load zero for all zones
Hi Aber,In "Zone Control Type Sched" you need to use SummerDesignDay and WinterDesignDay instead of SummerTypical and WinterTypical.--KarenOn Mon, Jan 21, 2013 at 11:36 PM, Aber Alvi <aberalvi@xxxxxxxxx> wrote:Hi Karen,Yes, below is the control type schedule and I have given the single heating and cooling set point schedule I used in my email below. These schedules apply to all zones.
Zone Control Type Sched, !- NameControl Type, !- Schedule Type Limits NameThrough: 12/31, !- Field 1For: SummerTypical, !- Field 2Until: 24:00, !- Field 32, !- Field 4For: WinterTypical, !- Field 5Until: 24:00, !- Field 61, !- Field 7For: AllOtherDays, !- Field 8Until: 24:00, !- Field 90; !- Field 10Thanks,Aber
From: Karen Walkerman <kwalkerman@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Monday, January 21, 2013 9:02 PM
Subject: Re: [EnergyPlus_Support] Calculated cooling and heating load zero for all zones
Do you have a ZoneControl:Thermostat object?On Jan 21, 2013 10:46 AM, "Aber Alvi" <aberalvi@xxxxxxxxx> wrote:Another thing I notice in the sensible heat gain summary of the output report of the same file is that opaque surface conduction and other heat addition is zero for zones with surfaces exposed to the ambient. The exposed surfaces boundary condition type is outdoor and is exposed to the sun and wind. Any idea why this could be happening?Thanks,Aber
From: Aber Alvi <aberalvi@xxxxxxxxx>
To: "EnergyPlus_Support@xxxxxxxxxxxxxxx" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, January 14, 2013 11:23 AM
Subject: [EnergyPlus_Support] Calculated cooling and heating load zero for all zones
Hi,I'm getting the following warning for all the zones while trying to model a building located in climate zone 1.** Warning ** Calculated design cooling load for zone=OS:THERMALZONE 7 is zero.** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.** Warning ** Calculated design heating load for zone=OS:THERMALZONE 7 is zero.** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.I've used the following single heating and single cooling setpoint schedule using SizingPeriod:WeatherFileConditionType.
Schedule:Compact,Htg-SetP-Sch, !- NameTemperature, !- Schedule Type Limits NameThrough: 12/31, !- Field 1For: WinterTypical, !- Field 2Until: 24:00, !- Field 321; !- Field 4For: SummerTypical, !- Field 5Until: 24:00, !- Field 611; !- Field 7For: AllOtherDays, !- Field 8Until: 24:00, !- Field 921; !- Field 10
Schedule:Compact,Clg-SetP-Sch, !- NameTemperature, !- Schedule Type Limits NameThrough: 12/31, !- Field 1For: SummerTypical, !- Field 2Until: 24:00, !- Field 323; !- Field 4For: WinterTypical, !- Field 5Until: 24:00, !- Field 650; !- Field 7For: AllOtherDays, !- Field 8Until: 24:00, !- Field 923; !- Field 10I have used ZoneInfiltration:DesignFlowRate for the infiltration of 1.024 l/s/m2 using flow/exteriorarea as the design flow rate calculation method. I have also checked the internal gain inputs and they don't seem to be too high or low. The lighting power is in line with ASHRAE 90.1 requirements, number of people is 0.04 person/m2 and equipment load is 2.7 W/m2.Any suggestions?Thanks,Aber
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___