Thank you all for your help!
I followed Brent's directions and set the heating setpoint
temperature to a higher value than the zone mean air temperature
for the WinterDesignDay only and it worked! The system is properly
sized, never turns on and there are no unmet setpoint
temperatures.
And this is the schedule:
Schedule:Compact,
Heating Setpoint IndCond Schedule, !- Name
Temperature, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: WinterDesignDay, !- Field 2
Until: 24:00, !- Field 3
20, !- Field 4
For: AllOtherDays, !- Field 5
Until: 24:00, !- Field 6
-18; !- Field 7
On 6.12.2012 19:42, Griffith, Brent wrote:
Hi Miroslav,
This error is
occurring during sizing of the air handler, not
operation. You need the sizing results to not come
out zero. Probably want to schedule some loads to be
“on” and/or disable whatever indirect conditioning is
taking all the load during design day types.
Schedules can be setup to define different things to
happen for the day types called WinterDesignDay and
SummerDesignDay.
Brent
Hello James,
All the zones connected to this air loop have no
loads. They are all indirectly conditioned.
I think that if I use normal setpoints with
always off availability, it will result in hours
with unmet setpoints.
On 6.12.2012 01:39, Jim Dirkes wrote:
Miroslav,
I’m
guessing that this is the only air loop…
I have modeled other buildings where one
or another zone had zero load, but always
at least one zone had load – with no fatal
errors.
How
about using normal setpoints and making
the availability always OFF?
James V Dirkes II, PE, BEMP,
LEED AP
www.buildingperformanceteam.com
Energy
Analysis, Commissioning & Training
Services
1631
Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
James,
The program stops before the actual
simulation. This is the full message
from the .err file.
** Severe ** AirLoopHVAC
AHU-RHT_BL has no air flow
** ~~~ ** Check flow rate
inputs for components in this air
loop and,
** ~~~ ** if autosized, check
Sizing:Zone and Sizing:System
objects and related inputs.
** Fatal ** Previous condition
causes termination.
...Summary of Errors that led to
program termination:
..... Reference severe error
count=1
..... Last severe
error=AirLoopHVAC AHU-RHT_BL has no
air flow
************* Warning: Node
connection errors not checked - most
system input has not been read (see
previous warning).
************* Fatal error --
final processing. Program exited
before simulations began. See
previous error messages.
On 6.12.2012 00:04, Jim Dirkes
wrote:
Ignore
the “error”. It does not
prevent the simulation from
running and, as you said,
indicates a correct and proper
condition.
E+
is just letting you know about
an unusual condition.
James
V Dirkes II, PE, BEMP,
LEED AP
www.buildingperformanceteam.com
Energy
Analysis, Commissioning
& Training Services
1631
Acacia Drive, Grand Rapids,
MI 49504 USA
616 450 8653
Hello all,
I have a building with
some indirectly
conditioned spaces and I
am
modeling a system (PVAV
with reheat) just to
satisfy the requirement of
Appendix G that all
conditioned spaces should
be simulated as both
heated and cooled. I set
higher and lower setpoint
temperatures for the
heating and cooling
respectfully, so the
system would never turn
on. But
during the simulation I
get a severe error which
says that AirLoopHVAC
has no air flow. Of course
this is absolutely correct
since there are no
any loads.
I wonder if anyone has had
such case and what's the
way to deal with
this problem?
Any help is highly
appreciated!
Thank you!
Miroslav
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|