[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: Why Autosize does not consider System Outdoor Air Loads





Check which node the Coil Controller is referencing and output the setpoint being set on that node. Output your mass flowrate and temperature water side for the coil.


2014-07-08 16:44 GMT+02:00 HJ wanghaojie630@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

Thank you very much Annie. For the air flow rate in the airloop, I manage to get it right now. It is now correctly based on the ventilation requirement. I also made the change on the plant sizing delta T and VAV minimum airflow. But the problem I still have is that the heating coil does not seem to heating up the air at all.
This is extracted from design day:

Before Heating coil:-15.45871895 C    After heating coil:    -15.45599013 C

Even though my room temperature is much lower than my heating setpoint temperature.

 I tried with only the dedicated outdoor air system in the model (without radiant system). E+ now will heat up the air a little bit, but still doesn't meet the central heating supply air temperature defined in sizing system. Is this because I used VAV with no reheat and sized by ventilation requirement? I dont have problem with traditional VAV with reheat to provide heating, cooling and ventilation. I only see this problem when I use VAV to supply ventilation air only and precondition it to 12.78 C.

Thanks again for you time.

These are my sizing zone and system information.

Sizing:Zone,
    Thermal Zone 9,          !- Zone or ZoneList Name
    SupplyAirTemperature,    !- Zone Cooling Design Supply Air Temperature Input Method
    12.78,                   !- Zone Cooling Design Supply Air Temperature {C}
    ,                        !- Zone Cooling Design Supply Air Temperature Difference {deltaC}
    SupplyAirTemperature,    !- Zone Heating Design Supply Air Temperature Input Method
    30.5556,                 !- Zone Heating Design Supply Air Temperature {C}
    ,                        !- Zone Heating Design Supply Air Temperature Difference {deltaC}
    0.0085,                  !- Zone Cooling Design Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.008,                   !- Zone Heating Design Supply Air Humidity Ratio {kgWater/kgDryAir}
    ASHRAE_189.1-2009 ClimateZone 4-8 SecondarySchool Library Ventilation,  !- Design Specification Outdoor Air Object Name
    ,                        !- Zone Heating Sizing Factor
    ,                        !- Zone Cooling Sizing Factor
    DesignDay,               !- Cooling Design Air Flow Method
    0,                       !- Cooling Design Air Flow Rate {m3/s}
    0.000762,                !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
    0,                       !- Cooling Minimum Air Flow {m3/s}
    0,                       !- Cooling Minimum Air Flow Fraction
    DesignDay,               !- Heating Design Air Flow Method
    ,                        !- Heating Design Air Flow Rate {m3/s}
    0.002032,                !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
    0.1415762,               !- Heating Maximum Air Flow {m3/s}
    0.3,                     !- Heating Maximum Air Flow Fraction
    Thermal Zone 9 Design Spec Zone Air Dist;  !- Design Specification Zone Air Distribution Object Name


!-   ===========  ALL OBJECTS IN CLASS: SIZING:SYSTEM ===========

Sizing:System,
    VAV with Reheat,         !- AirLoop Name
    VentilationRequirement,  !- Type of Load to Size On
    Autosize,                !- Design Outdoor Air Flow Rate {m3/s}
    0,                       !- Minimum System Air Flow Ratio
    12.78,                   !- Preheat Design Temperature {C}
    0.008,                   !- Preheat Design Humidity Ratio {kgWater/kgDryAir}
    12.78,                   !- Precool Design Temperature {C}
    0.008,                   !- Precool Design Humidity Ratio {kgWater/kgDryAir}
    12.78,                   !- Central Cooling Design Supply Air Temperature {C}
    40,                      !- Central Heating Design Supply Air Temperature {C}
    NonCoincident,           !- Sizing Option
    Yes,                     !- 100% Outdoor Air in Cooling
    Yes,                     !- 100% Outdoor Air in Heating
    0.0085,                  !- Central Cooling Design Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.008,                   !- Central Heating Design Supply Air Humidity Ratio {kgWater/kgDryAir}
    DesignDay,               !- Cooling Design Air Flow Method
    ,                        !- Cooling Design Air Flow Rate {m3/s}
    DesignDay,               !- Heating Design Air Flow Method
    ,                        !- Heating Design Air Flow Rate {m3/s}
    ZoneSum;                 !- System Outdoor Air Method






On 7/8/2014 8:45 AM, annie anniemarston@xxxxxxxxxxx [EnergyPlus_Support] wrote:
 

Hi,

I model these systems a lot and so I took a quick look at your file. Two things struck me straight away

1. Plant sizing object has a delta T of 2.2°K on the hot water loop. This seems to me like a very small delta T for a hot water loop, mine is usually closer to 20°K

2. You have a VAV no reheat object
AirTerminal:SingleDuct:VAV:NoReheat,
    AT9,                     !- Name
    Always On Discrete,      !- Availability Schedule Name
    Node 180,                !- Air Outlet Node Name
    Node 186,                !- Air Inlet Node Name
    autosize,                !- Maximum Air Flow Rate {m3/s}
    Constant,                !- Zone Minimum Air Flow Input Method
    0,                       !- Constant Minimum Air Flow Fraction
    ,                        !- Fixed Minimum Air Flow Rate {m3/s}
    ,                        !- Minimum Air Flow Fraction Schedule Name
    ASHRAE_189.1-2009 ClimateZone 4-8 SecondarySchool Library Ventilation;  !- Design Specification Outdoor Air Object Name

Which is asking that the minimum air flow input is constantly zero. Changing this value could help.

It might also help to change the rated inlet air temperature on your heating coils from 16.6°C to something much lower, that way the coils will size larger. It is also likely that the temperature coming into these coils will be cooler than 16.6°C.

Annie


To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
Date: Mon, 7 Jul 2014 18:32:30 -0400
Subject: Re: [EnergyPlus_Support] Re: Why Autosize does not consider System Outdoor Air Loads [1 Attachment]

 
Thanks. I attached a file that has a radiant system and a DOAS and four pipe fan coil to serve mechanical and restrooms. The DOAS will supply 12.8 C air temperature (by setpoint manager) all time (no reheat VAV box). The radiant system will provide cooling and heating to meet the rest of the load. Now my problem is during heating time, there is no air flow at all going through the DOAS system. I tried to increase the minimum airflow rate passing the VAV box to 0.3, now I see airflow rate but the supply air temperature is the same as outdoor air temperature (no heating at all). I would really appreciate if someone could look into this file and help me with this. This seems really strange to me because basically E+ thinks there is no zone load or ventilation load at all during heating time. (Cooling works fine though)

HJ



On 7/7/2014 11:58 AM, Jean Marais jeannieboef@xxxxxxxxx [EnergyPlus_Support] wrote:
 
Well then if your system supply temperature is not 30 C but 13 C, then leave the sizing:zone object with the 30 C for heating (and I think you said 17 C for cooling) and introduce some extra load by some other means...you could for example consider the enthalpy difference from 13 C 100%RH to 20 C at the given flowrate of your AHU (min ODA) and put in a negative process load equalling that (you may need to adjust your idd file to accommidate negative process loads.


2014-07-07 17:26 GMT+02:00 HJ wanghaojie630@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 
The problem I have during sizing period is that the room temperature is only 10C when I have radiant plus  radiant system serving the zone. During annual simulation, this problem disappear and I think it is due to the higher internal load such as people and receptacle (they are zero during winter design day). I think the problem that causing the room temperature so low is the radiant system sizing is only for zone load but not ventilation load (ventilation SA Temp is 13 C, so it need to be heated up to 20C as the heating setpoint by radiant system).

HJ



On 7/7/2014 9:57 AM, Jean Marais jeannieboef@xxxxxxxxx [EnergyPlus_Support] wrote:
 
It will work as long as the supply air temperature in hte sizing:zone object can combat the zone load (so for heating it must be more than the zone heating setpoint, and for cooling less than the zone cooling setpoint). In your sizing:system object you set the design supply air temperature as what you expect the air side system to bring (that excludes fancoils which are not system equipment, but zone equipment).The ADU sizing routine has a flag that will properly size the ADU on ventilation rate if the sizing:system object uses ventilation rate as the sizing method, otherwise it is sized from the information from the sizing:zone object.


2014-07-07 15:41 GMT+02:00 HJ wanghaojie630@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 
Thanks Jean. So for example, if I have heating setpoint of 20C. My DOAS is supplying 13 C and the sizing:system is also set as 13 C for central heating, but the sizing:zone heating supply air temperature is set as 30C. Will it properly size the system? The problem is that I have radiant system but the only place I can specify the water temperature is in sizing:plant. From the  EnergyPlus engineering reference, it says the sizing:zone will perform first to calculate how much air flow needed based on supply air temperature (specified in sizing:zone) and zone load. Then sizing:system will run to calculate the air system side. Then sizing:plant will run to calculate the plant water flow rate. However, based on this sequence, I think it will not work properly for radiant system. Or maybe they use different procedure for radiant system?

Thanks,

HJ



On 7/4/2014 1:06 AM, 'jeannieboef@xxxxxxxxx' jeannieboef@xxxxxxxxx [EnergyPlus_Support] wrote:
 
Hi Karen, as soon as you posted this, I went to test it, because it messes up my current understanding of the autosizing in e+. For Germàn's case, it does not work and fits my current mental model. For HJ's case, it would work as long as the zone setpoint is able to be corrected by the system's air supply. So if he has a zone heating setpoint of 20 and is trying to heat with 13 C system supply air, it will not size the equipment properly and the issue is the same as Germàn's.  

Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity)

i. A.
Jean Marais
b.i.g. bechtold

On 03.07.2014, at 23:53, "Karen Walkerman kwalkerman@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 

I think that you might not be setting the design heating and cooling supply air temperatures correctly in the Sizing:System object. If you have an air handler providing unconditional ventilation air to zones, set the design heating temperature equal to the outdoor temperature of your heating design day at the system level. Same with cooling. Then your ZoneHVAC equipment should size correctly.

Karen

On Jul 3, 2014 12:30 PM, "HJ wanghaojie630@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 
Thanks. I misspoke, actually s1 provide 13 air temperature all time. So in summer it provide some cooling, and winter it preheat air to 13 C. In this case, will s2 be oversized for summer and undersized for winter?


HJ



On 7/3/2014 12:16 PM, ecoeficiente@xxxxxxxxx [EnergyPlus_Support] wrote:
 
In your case, s2 will only be sized for zone loads without accounting for s1 ventilation load. But, as you say, your s1 system provides neutral air temperature, that is, no load. In that case you do not have the problem I mentioned.

Regards.











__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___