[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: Why Autosize does not consider System Outdoor Air Loads





My text editor (and many others) can do a text highlighting side-by-side comparison to find the differences between the two files. If you can't do that, I would be happy to check it for you to find the difference/problem.
Perhaps you had a decimal point intead of a comma or visa verse, or some field that was not allowed to be blank and was auto-fixed in Open Studio.

Mit freundlichen GrüÃ?en- Sent from my iPhone (excuse the brevity)

i. A.
Jean Marais
b.i.g. bechtold
Tel.   +49 30 6706662-23

On 10.07.2014, at 17:21, "HJ wanghaojie630@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 

Thanks Jean, i checked with it and it seems it does not provide any water flow even though the setpoint is higher than the node temeprature (heating). I recreate a airloop using Openstudio and now seems everything is fine. Maybe I accidentally changed something.... But now it seems to be working. Thanks again.

HJ


On 7/8/2014 11:39 AM, Jean Marais jeannieboef@xxxxxxxxx [EnergyPlus_Support] wrote:
 
Check which node the Coil Controller is referencing and output the setpoint being set on that node. Output your mass flowrate and temperature water side for the coil.


2014-07-08 16:44 GMT+02:00 HJ wanghaojie630@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

Thank you very much Annie. For the air flow rate in the airloop, I manage to get it right now. It is now correctly based on the ventilation requirement. I also made the change on the plant sizing delta T and VAV minimum airflow. But the problem I still have is that the heating coil does not seem to heating up the air at all.
This is extracted from design day:

Before Heating coil:-15.45871895 C    After heating coil:    -15.45599013 C

Even though my room temperature is much lower than my heating setpoint temperature.

 I tried with only the dedicated outdoor air system in the model (without radiant system). E+ now will heat up the air a little bit, but still doesn't meet the central heating supply air temperature defined in sizing system. Is this because I used VAV with no reheat and sized by ventilation requirement? I dont have problem with traditional VAV with reheat to provide heating, cooling and ventilation. I only see this problem when I use VAV to supply ventilation air only and precondition it to 12.78 C.

Thanks again for you time.

These are my sizing zone and system information.

Sizing:Zone,
    Thermal Zone 9,          !- Zone or ZoneList Name
    SupplyAirTemperature,    !- Zone Cooling Design Supply Air Temperature Input Method
    12.78,                   !- Zone Cooling Design Supply Air Temperature {C}
    ,                        !- Zone Cooling Design Supply Air Temperature Difference {deltaC}
    SupplyAirTemperature,    !- Zone Heating Design Supply Air Temperature Input Method
    30.5556,                 !- Zone Heating Design Supply Air Temperature {C}
    ,                        !- Zone Heating Design Supply Air Temperature Difference {deltaC}
    0.0085,                  !- Zone Cooling Design Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.008,                   !- Zone Heating Design Supply Air Humidity Ratio {kgWater/kgDryAir}
    ASHRAE_189.1-2009 ClimateZone 4-8 SecondarySchool Library Ventilation,  !- Design Specification Outdoor Air Object Name
    ,                        !- Zone Heating Sizing Factor
    ,                        !- Zone Cooling Sizing Factor
    DesignDay,               !- Cooling Design Air Flow Method
    0,                       !- Cooling Design Air Flow Rate {m3/s}
    0.000762,                !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
    0,                       !- Cooling Minimum Air Flow {m3/s}
    0,                       !- Cooling Minimum Air Flow Fraction
    DesignDay,               !- Heating Design Air Flow Method
    ,                        !- Heating Design Air Flow Rate {m3/s}
    0.002032,                !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
    0.1415762,               !- Heating Maximum Air Flow {m3/s}
    0.3,                     !- Heating Maximum Air Flow Fraction
    Thermal Zone 9 Design Spec Zone Air Dist;  !- Design Specification Zone Air Distribution Object Name


!-   ===========  ALL OBJECTS IN CLASS: SIZING:SYSTEM ===========

Sizing:System,
    VAV with Reheat,         !- AirLoop Name
    VentilationRequirement,  !- Type of Load to Size On
    Autosize,                !- Design Outdoor Air Flow Rate {m3/s}
    0,                       !- Minimum System Air Flow Ratio
    12.78,                   !- Preheat Design Temperature {C}
    0.008,                   !- Preheat Design Humidity Ratio {kgWater/kgDryAir}
    12.78,                   !- Precool Design Temperature {C}
    0.008,                   !- Precool Design Humidity Ratio {kgWater/kgDryAir}
    12.78,                   !- Central Cooling Design Supply Air Temperature {C}
    40,                      !- Central Heating Design Supply Air Temperature {C}
    NonCoincident,           !- Sizing Option
    Yes,                     !- 100% Outdoor Air in Cooling
    Yes,                     !- 100% Outdoor Air in Heating
    0.0085,                  !- Central Cooling Design Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.008,                   !- Central Heating Design Supply Air Humidity Ratio {kgWater/kgDryAir}
    DesignDay,               !- Cooling Design Air Flow Method
    ,                        !- Cooling Design Air Flow Rate {m3/s}
    DesignDay,               !- Heating Design Air Flow Method
    ,                        !- Heating Design Air Flow Rate {m3/s}
    ZoneSum;                 !- System Outdoor Air Method






On 7/8/2014 8:45 AM, annie anniemarston@xxxxxxxxxxx [EnergyPlus_Support] wrote:
 

Hi,

I model these systems a lot and so I took a quick look at your file. Two things struck me straight away

1. Plant sizing object has a delta T of 2.2°K on the hot water loop. This seems to me like a very small delta T for a hot water loop, mine is usually closer to 20°K

2. You have a VAV no reheat object
AirTerminal:SingleDuct:VAV:NoReheat,
    AT9,                     !- Name
    Always On Discrete,      !- Availability Schedule Name
    Node 180,                !- Air Outlet Node Name
    Node 186,                !- Air Inlet Node Name
    autosize,                !- Maximum Air Flow Rate {m3/s}
    Constant,                !- Zone Minimum Air Flow Input Method
    0,                       !- Constant Minimum Air Flow Fraction
    ,                        !- Fixed Minimum Air Flow Rate {m3/s}
    ,                        !- Minimum Air Flow Fraction Schedule Name
    ASHRAE_189.1-2009 ClimateZone 4-8 SecondarySchool Library Ventilation;  !- Design Specification Outdoor Air Object Name

Which is asking that the minimum air flow input is constantly zero. Changing this value could help.

It might also help to change the rated inlet air temperature on your heating coils from 16.6°C to something much lower, that way the coils will size larger. It is also likely that


__._,_.___

Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___